Hi @Rui_Frontwell ,
In OPCUA - Critical Manufacturing Developer Portal you have already, some information. The tests depend a lot on your context and the type of testing that you are doing. We support tests that mock the MES and tests against a system. All of this is configured through plugins in the scenario configuration.
We have an example using REST Server at mes-common-library/features/IoTMTConnect/IoTMTConnect.Tests/IoTMTConnect.Tests.IoT/Tests/MTConnect.cs at 11.3/dev · criticalmanufacturing/mes-common-library
[TestInitialize]
public void Initialize()
{
PORT = new Random().Next(5000, 30000);
MASTERDATA = Path.Combine(Path.GetTempPath(), $"{TestContext.TestName}-{Guid.NewGuid():N}.json");
File.WriteAllText(MASTERDATA, File.ReadAllText(MASTERDATA_TEMPLATE).Replace("__DEFAULTPORT__", PORT.ToString()));
Configuration = new ScenarioConfiguration()
//Configure IoT Manager
.ManagerId("MTConnectManager")
.WriteLogsTo(Path.Combine(Path.GetTempPath(), $"{TestContext.TestName}-{Guid.NewGuid():N}-logs.txt"))
.Config(new Common.Objects.Config.ConfigBuilder()
.CacheLocation(Path.GetTempPath())
.Build())
// Settings for starting IoT manager
.StartMode<LocalStartMode.PluginMain>(new LocalStartMode.Plugin.SettingsBuilder()
.ManagerLocation(Path.Join(PACKAGES_LOCATION, MANAGER))
.UseOtlpLogging(false)
.Build())
// Configure MES Mock System
.SystemPlugin<MockSystem.PluginMain>(new MockSystem.Plugin.SettingsBuilder()
.Repository(PACKAGES_LOCATION)
// .Port(49202)
.MasterdataPath(MASTERDATA)
.AddSite("TestSite")
.AddManager("MTConnectManager")
.AddControllerInstance("Demo MTConnect Controller [A.1]", "MTConnectManager", "TestSite")
.AddDriverInstance("Demo MTConnect Controller [A.1]", "MTConnect", "MTConnectManager", "TestSite")
.Build())
// Configure the equipment simulator
.AddSimulatorPlugin<RestServer.PluginMain>(new RestServer.Plugin.SettingsBuilder()
.Address("http://0.0.0.0", PORT)
.Build());
}
Note that the difference to your use case is the configuration of the Simulator Plugin.
The driver OPC-UA buy using the DriverInstanceAlias (e.g .DriverInstanceAlias(“OPCUA”)), replicates the tags you have configured in your system and will automatically host them in an OPC-UA server. I believe this is currently only working for the scenario where your test runs against the MES.
var opcuaBuilder = new IoTTestOrchestrator.OPCUA.Plugin.SettingsBuilder()
.Address(opcuaAddress)
.DriverInstanceAlias("OPCUA");
You can also declare them one by one or through a json file.
var opcuaBuilder = new IoTTestOrchestrator.OPCUA.Plugin.SettingsBuilder()
.Address(opcuaAddress)
.AddTag(new OpcTag()
{
Name = $"Humidity",
NodeId = $"ns=2;s=Humidity",
AccessMode = AccessMode.ReadAndWrite,
Value = JsonSerializer.SerializeToElement(45.5),
Type = "Float"
}, "CNC0001")
.DriverInstanceAlias("OPCUA");
var opcuaBuilder = new IoTTestOrchestrator.OPCUA.Plugin.SettingsBuilder()
.Address(opcuaAddress)
.AddTagsFromJSON(File.ReadAllText(Path.Combine(assetDirectory, "JsonTags", "tags.json")))
.DriverInstanceAlias("OPCUA");
Example json:
{
"NodeTree": [
{
"NodeBranch": "CNC0001",
"Nodes": [
{
"Name": "ns=2;s=Temperature",
"Id": "Temperature",
"Type": "String",
"Value": "100",
"AccessMode": "ReadAndWrite"
},
{
"Name": "ns=2;s=QualiVision.MESAdapter.JobsStatus.JobsStatus",
"Id": "JobStatus",
"Type": "Custom",
"CustomDataType": "QualiVision.opcuabb.Job",
"Value": {},
"AccessMode": "ReadAndWrite"
},
{
"Name": "ns=2;s=QualiVision.MESAdapter.ShiftViewStatus.ShiftViewStatus",
"Id": "ShiftViewStatus",
"Type": "Custom",
"CustomDataType": "QualiVision.opcuabb.TimeBoxData",
"Value": {},
"AccessMode": "ReadAndWrite"
},
{
"Name": "ns=2;s=TestCustomProperty",
"Id": "TestCustomProperty",
"Type": "String",
"Value": "",
"AccessMode": "ReadAndWrite"
},
{
"Name": "ns=2;s=CodeCustomProperty",
"Id": "CodeCustomProperty",
"Type": "Double",
"Value": 0,
"AccessMode": "ReadAndWrite"
},
{
"Name": "ns=3;s=namespace_three_string_address",
"Id": "namespace_three_string_address",
"Type": "String",
"Value": "100",
"AccessMode": "ReadAndWrite"
},
{
"Name": "ns=3;i=101",
"Id": "namespace_three_numeric_address",
"Type": "String",
"Value": "100",
"AccessMode": "ReadAndWrite"
},
{
"Name": "ns=3;s=AirConditioner_9.Humidity",
"Id": "HumidityCT",
"Type": "Double",
"Value": 53,
"AccessMode": "ReadAndWrite"
},
{
"Name": "ns=3;s=AirConditioner_1.PowerConsumption",
"Id": "PowerConsumptionCT",
"Type": "Double",
"Value": 122,
"AccessMode": "ReadAndWrite"
}
]
}
]
}
There are other configurations like commands, file server and server side events:
var opcuaBuilder = new IoTTestOrchestrator.OPCUA.Plugin.SettingsBuilder()
.Address(opcuaAddress)
.AddNamespace("urn:yourcompany:default:v1")
.AddNamespace("urn:yourcompany:machines:v1")
// Register real OPC UA custom methods ahead of server start
.AddCustomCommand(new IoTTestOrchestrator.OPCUA.Plugin.CustomCommandBuilder("fbiGetData", "ns=2;s=prgMES.fbiGetData#Methode", "ns=2;s=prgMES.fbiGetData")
.Output("Result", "String")
.Build())
.AddCustomCommand(new IoTTestOrchestrator.OPCUA.Plugin.CustomCommandBuilder("fbiPrepareEquipment", "ns=2;s=prgMES.fbiPrepareEquipment#Methode", "ns=2;s=prgMES.fbiPrepareEquipment")
.Input("Command", "UInt16")
.Build())
.AddCustomCommand(new IoTTestOrchestrator.OPCUA.Plugin.CustomCommandBuilder("StartMachine", "ns=2;s=Machines/Machine_1/StartMachine", "ns=2;s=Machines/Machine_1")
.Build())
.AddCustomDataTypesFromJson(JobStatusCustomDataTypesJson)
.AddTagsFromJSON(File.ReadAllText(Path.Combine(assetDirectory, "JsonTags", "tags.json")))
.AddCustomEvent(Path.Combine(assetDirectory, "CustomTemplates", "CustomEvent.json"))
.AddCustomEvent(Path.Combine(assetDirectory, "CustomTemplates", "CustomTemplateEventPropExtendedData.json"))
.FileServer(Path.Combine(assetDirectory, "TestFileServer"))
.DriverInstanceAlias("OPCUA");
For the test itself,
[TestMethod]
public void OPCUAReadAndWriteTagTemperature()
{
#region Setup
var controllerInstance = testContext.Instances["Controller"] as IControllerInstanceContext;
var controllerInstanceContext = controllerInstance as IInstanceContext;
var driverInstanceLog = (testContext.Instances["OPCUA"] as IInstanceContext).Log;
#endregion Setup
// Utility to make sure that the event was created and subscribed
testScenario.Utilities.WaitFor(30, "TemperatureChanged subscription heartbeat was not received", () =>
{
return driverInstanceLog.Any(log =>
log.Contains("Subscription Heartbeat for event 'TemperatureChanged'", StringComparison.OrdinalIgnoreCase));
});
var expectedTemperature = Random.Shared.Next(200, 1000).ToString();
// Set a tag value in the simulator
opcuaSimulator.WriteTag("Temperature", expectedTemperature);
// Check temperature was writter
Assert.AreEqual(expectedTemperature, opcuaSimulator.ReadTag("Temperature")?.ToString());
controllerInstanceContext.Log.Clear();
using var replyReceived = new ManualResetEventSlim(false);
string replyValue = string.Empty;
Exception replyHandlerError = null;
// Calls via messagebus a system event listener to trigger a tag read and waits for the reply and validates it
controllerInstance.SystemEvent("Cmf.Test.OPCUA.ReadTag.Temperature", "This should trigger a GetEquipmentValue and receive back the value read", IoTTestOrchestrator.Common.Objects.WebSockets.SendType.SendRequest, (message) =>
{
try
{
var content = JObject.Parse(message);
replyValue = content["reply"]?.ToString() ?? string.Empty;
if (string.IsNullOrWhiteSpace(replyValue))
{
replyHandlerError = new InvalidOperationException($"Reply payload did not contain 'reply': {message}");
}
}
catch (Exception ex)
{
replyHandlerError = ex;
}
finally
{
replyReceived.Set();
}
});
Assert.IsTrue(replyReceived.Wait(TimeSpan.FromSeconds(15)), "Expected reply was not received");
if (replyHandlerError != null)
{
Assert.Fail($"Failed to parse the reply payload: {replyHandlerError}");
}
Assert.AreEqual(expectedTemperature, replyValue);
// Check via logs that the read read happened and was emitted
testScenario.Utilities.WaitFor(15, "Expected controller logs not found after reply was received", () =>
{
var liveLog = controllerInstanceContext.Log;
var escapedExpectedTemperature = Regex.Escape(expectedTemperature);
var hasPropertyLog = liveLog.Any(log =>
Regex.IsMatch(log, $@"\|ReadTag\|.*\|getEquipmentProperties\] Emitting property value 'Temperature'='{escapedExpectedTemperature}'")
);
var hasRawLog = liveLog.Any(log =>
Regex.IsMatch(log, $@"\|ReadTag\|.*\|logMessage\] {escapedExpectedTemperature}")
);
return hasPropertyLog && hasRawLog;
});
}
For invoking a command, the test application needs to register in the scenario and the invoke the workflow in a way that calls the command. For example:
[TestMethod]
public void ExecuteCommandInCustomDriverDef()
{
#region Setup
var controllerInstance = testContext.Instances["Controller"] as IControllerInstanceContext;
var controllerInstanceLog = (controllerInstance as IInstanceContext).Log;
#endregion Setup
// Publish message bus message that is picked up by a workflow and calls an OPC-UA Command
var mbClient = system.NewMessageBusClient();
mbClient.Publish("Cmf.Test.OPCUA.ExecuteCustomCommand", new
{
});
// Will call the "ns=2;s=Machines/Machine_1/StartMachine" command
testScenario.Utilities.WaitFor(10, "Failed to execute command", () =>
{
return controllerInstanceLog.Any(log =>
Regex.IsMatch(log, $@"\|ExecuteCustomCommand\|.*\|logMessage\] Got Success on ExecuteCommand Output")
);
});
}